My original statement was:A GFCI does not require a Safety Ground (EGC) reference! The GFCI only examines the current in the Send and Return wires, if these are not equal (5ma) then the unit trips.Just how is that statement incorrect?***************************************************from your first link: Don't let the name confuse you — these devices will operate on a circuit that does not have an equipment-grounding conductor.
The GFCI does not need or use a external reference. It is only aware of the current in the Send and Return wires. As long as these two currents are about equal the GFCI is happy. In any case, current is not interested in going to the ground or into the dirt, it is only interested in getting back ti it's source which is that big power company transformer outside.
Thank you Occam for the drawing.To Jea48As for the service neutral conductor / earth /equipment enclosure/ equipment ground be bonded at only one location at the main electrical service of the building we do not know that it is not.Please refer to the photo from the OP, it clearly shows the neutral conductor being bonded to discoloured copper cables, which eventually end up on the metal conduits. The neutral in then bonded to earth, not in a manner that's normal, surely.Another point of using GFCI/RCD is that if the earth conductor is broken on say a toaster or an appliance outside, if someone touches the live portion of the appliance while say touching a tap/faucet, the GFCI will trip.In your first test, if you wired the device correctly, the GFCI should have tripped. If it didn't, it's great you found a dud. The RCD is supposed to trip since it artificially creates an imbalance of current around the CT, rather than through it.
Agreed, GFCI can be used on floating supplies. To Jea48, how then are delta/delta transformers protected, since there is no common star point?
FWIW
One and a half, I am still waiting for your answer on how the "Test" circuit works in the diagram Occam provided in his post.
By pushing the test button, this allows a current to flow through the CT since the resistor is connected across the two incoming lines (not marked in the drawing as to the input).The resistor current returns to the upstream connection bypassing the CT. Since the current drawn by the resistor is not cancelled out by the return wire from the resistor, the CT and electronics measure the difference in current I load + I resistor. If the I resistor current is more than the device's sensitivity, the breaker will trip.Various GFCI are designed to measure either sine waves, or pulsed currents for example from rectifiers/SMPS. The device needs to be correctly specified for the intended function. More reading: https://www.hqs.sbt.siemens.com/gip/general/dlc/data/assets/hq/manual/beta_all_technology-primer-rcpd_tpi_en.pdfThe circuit does not require any of the main conductors (Hot & neutral) to be grounded, since grounding is not relevant for displacement currents. So long as the load current remains symmetrical, the GFCI will hold.Typical current paths. The lady's "fault current" is only seen by one leg of the CT, the GFCI will trip.For a 3phase network, here's a schematic showing the terminals.You are correct, nothing will prevent a line to line load from operating a GFCI, if that load were a person. If the over current device works, then this may be the saving grace and applies equally to systems protected or not protected by GFCI. And the point of which is?
Look at it this way, a typical home has a single phase 240V (120/120) service. If the GFCI circuit is connected to the 'A' leg/pole (aka phase) and it's Hot 120V wire leaks to the 'B' leg's Hot 120V. There will be leakage current (after all these two Hots are 240 Volts apart) so the GFCI will trip.
We are talking about electrical power that can kill. I have only stuck with this thread in the hope of convincing the laymen reader that a GFCI will not protect a person from a lethal line to line shock if no other part of the person’s body is in contact with a grounded object.Second a GFCI WILL NOT provide any protection whats so ever when connected to a floating secondary of an ISO transformer.
Regardless of how many out of context or simplified examples you quote, this is incorrect!A GFCI device only asks one question:Is the amount of current on the Neutral the same amount as the Hot? If not - it trips. End of story, it does not know or care about what is causing that current difference.
Perhaps my point would be easier to grasp if for the word 'ground' in the above articles we substitute the concept of:"An accessible pathway for fault current to flow back to it's source and it's source is the power company Neutral"********************************'ground' is not a destination, it is a path.*******************************And once again, a GFCI device does not need to be connected to a Safety Ground (EGC) to operate correctly.
OK, here is the difference. You are looking at it from a theoretical system viewpoint. That is with an isolation transformer just where is the fault or leakage current going to go? But the GFCI does not look outside itself, all it can see is the current on the Hot & Neutral wires and if these two currents aren't the same but opposite then it trips. Now getting back to the real world, that ISO transformer might be good today but what about tomorrow?
Now please explain your theory of how or where a current imbalance could possibly take place for the sensing coil, of the GFI receptacle, to sense any imbalance If there is no current imbalance there is no safety problem. Now getting back to the real world, that ISO transformer might be good today but what about tomorrow?Not sure what you mean..... What I mean is when everything is operating correctly then everything is OK, but what happens if the transformer insulation fails? or a wire from another circuit somehow comes in contact with the ISO circuit.GFCI's are only important when things go wrong.