No. The ground for the cable was connected to a pipe in the ground in the front yard. I temporarily disconnected it and reconnected to the pipeing used for the new electrical outlets. The AC service box is in the downstairs and inside at the back of the house. Outside meter with an inside box. It is an 1100 square foot upstair dwelling. The cable box is on the North East corner and the AC power Box is on the Southwest Corner of the house. I'm going to estimate the distance from the cable box to the power box at 80Ft with consideration to the decking and such. The wireing downstairs is using modern three wire romex. The Wireing upstairs is two wire. When the inspection was done on the house prior to purchase the home inspector indicated that the GFI's downstairs were wired incorrectly. They were not grounded. The downstairs is a "Illegal" unit. It ia all modern construction. The upstairs is very old and is old style wireing. There is no labeling on the GFI's
Now this is the important part:Here is the rest, the part the installer missed. The ground rod or pipe shall connect to the main grounding system of the main electrical service by a copper wire minimum wire size #6 awg. An approved clamp shall be used to connect the #6 awg copper wire to the ground Rod or pipe.From our point of view (audio system) the ground rod construction matters not.The ground rod is only there for thunderstorms and the such.
The cable box is on the North East corner and the AC power Box is on the Southwest Corner of the house. I'm going to estimate the distance from the cable box to the power box at 80Ft with consideration to the decking and such.
STOP. Go no further.Fix that first and foremost.Cable MUST enter the building at the same location as the power. When that is done and it's all bonded properly, see if you still have a problem.jn
You guys are the best.In the front of the house there is the main water input for the home. The water goes from metal from the curb to plastic going into the house. I would bet that the water pipes inside the house walls are metal. Questions:Can I connect my cable ground to the metal water pipes coming off the curb?If I go into the wall and find metal water pipes can I connect my ground inside a wall? or does the plastic original connection to the curb pipes defeat the ground.I could send my girlfriend with cookies and coffee to say pretty please to the cable guys. They would have to run from the street to the back of the house then back to the front again. What do you think
Option....Is the basement ceiling finished? Could a #4 copper ground wire be ran from the front of the house to the back of the house where the main electrical panel is located?If it is possible the "Bonding Jumper Wire", fancy name for ground wire, could be installed from the ground pipe in front of the house through the basement fastened to the bottom of the floor joists, or ran through bored holes in the joists, to the grounding electrode wire that goes from the electrical panel to the outside ground rod/s. That would meet NEC Code.Note I said a #4 awg copper wire instead of a #6. Code is bare minimum. I would increase the wire to #4 because of the distance. I would use #4 bare solid copper wire.You would need to verify the driven pipe in the front yard is indeed 8 ft deep in the earth. Also it is at 3/4" galvanized or plated corrosion resistant pipe.The Cable Company installer would never be able to handle the job. The Cable Company would have to hire a Licensed electrician. The electrician may elect to drive a new 5/8” x 8ft ground rod in the front yard and not use the existing pipe.The electrician will also know if running the Bonding Jumper Wire through the house meets your local electrical inspection dept code. I do not see a problem With NEC Code. Will you still need to use the Jensen ISO transformer? Don't know. But you already have bought it and it is on its way.
I requested the appropriate wire size in my service request. The wire can be run under my deck on the side of the house to the backyard where it will be a Bonding Jumper Wire. I hope they do not have to have an electrician do the job. They may have to come back another day.
The Cable Guy moved everything to the back of the house and life is good. He just ran longer lengths of RF cable to the back then back to the front. I took the Jensen Cable transformer off the line. No Hum. I think I'll just put it back on the line and leave it there.Any objections?