Circuit #28 is not on the same phase as the other two circuits.
There is no "phase differential" in home wiring. You have 2 incoming 120 volt lines a neutral and a ground that goes to a copper rod, pounded into the ground, outside of your home. The 2 120 volt lines are in the same "phase" and when you put the two 120 volt lines (instead of 1 120 volt line and a neutral), you have 240 volt. It is all single phase.Wayner
Skip the theory. Go directly to experiment:The way to tell is:Each outlet has a hot, neutral, and ground.If you stick a voltmeter (suitable for Ac240 volts) into the hot and neutal you get 120 volts. Ditti the hot and ground, you get 120 volts.If you have another line, that duplex will be the same within itself.In they both are on the same 'leg' then connecting the two hots (using the voltmeter will give you zero volts.If they are NOT on the same leg, then that action of using the two hots will get you 240 volts.Ditto a third. so if you cross connect all three separate HOT runs and get zero volts from trying two hots each. AB BC AC.. then you are 100% absolute on one leg.If any combo gets you 240 volts. you are using two legs..That 240 volt potential IS the issue with using more than one leg of incoming power.Added: If as JerryM suggests the circuit #28 in not on the same phase as the other two.. then that hot connected to eiither of the other two hot wires is a potential of 240 volts.
I found the CAD drawings for this load center on Schneider's website. The important part is the set of schematics on the right-hand side of the drawing. Look at the one for your load center (QO140M200C). Breakers in the same row are always on the same hot. The rows alternate between the two hots. So, slots 27, 28, and 31 are all on the same hot.BTW, this arrangement is fairly common since it allows you to install 240v breakers like this: That's great information! Thank You.
VERY interesting. I wonder why my audio distributor told me this, and why my electrician was reciting "phase A, phase B" about 100 times?
And then if you are going to use say, an electric range that requires 240v to operate, how could you accomplish that with two 'legs' of the same 'phase'?
Can anyone out there please confirm if my three dedicated stereo lines are wired correctly and all on the same phase? The three stereo circuits in question are # 27, 28 and 31. Photos of the panel configuration, and SqareD model/information are attached for your review.
OK, then since both legs are same phase, is it necessary to put all audio gear on the same leg?If so, why?
Hi.All USA & Canadian home powerline distribution networks employ the same single-phase 3-wire midpoint neutral system.For audio use, I would hook up all dedicated powerlines from the same feeding line of the incoming HV duplex distribution lines. This is to ensure the same & equal HV voltage supplied to all the dedicated powerlines for yr audio. Why? Different loads of different household electrical lightings & appliances, resulting different voltage drop across each of 2 duplex feeding lining from the distribution transformer outside of yr house despite they both being in the same phase.In yr case, I suggest you to have the dedicated powerline now hooked up #28, connected to the same 'side' of terminals rack where #27 & #31 now hooked up to. By such reconnection, ALL yr 3 dedicated powerlines are sharing the same incoming feeding line of the duplex distribution system. So same & identical voltage will be supplied to all yr dedicated powerlines for yr audio.I'vd done it simple for my 2x 125V dedicated powelines as I only use one single larger gauge size RW90 cable hooked up to my house contactor panel to a dedicated 125V wall outlet, from where I branched out 2 dedicated powerlnes (each with inline RFI filter) to my analogue & digital gear discretely.c-J