"* X2 needs to be connected to the equipment chassis ground point. This makes X2 winding lead the neutral conductor. (The grounded Conductor) This will also connect to the silver color screw on the output duplex receptacle."Just want to triple check - I just grounded the shields to Chassis groundNow - we ground X2 AND the White wire to the same Chassis ground?see picCan I leave the white wired to X2 and I just run one wire from X2 to chassis ground ORdo I need to run Wire X2 to Chassis ground AND White wire to Chassis groundThen I will probably need to install spades to get all those wires to fit on one chassis ground screw lugsee pic
@jea. Thanks I will check
@jea48Wiring done - -on the iso trans output - hot to ground is 118V, neutral to ground is 0Vhowever, I checked the hot on the duplex outlet that the ISO trans plugs intoTO the hot connection coming OUT of the ISO Trans - this is 238VSo - the Iso trans output is Out of Phase with the input? I have a lamp plugged into the output of the iso trans now - seems ok
For now lets not address that. That's a simple change. First I would like you to measure for voltage from the hot contact of the duplex receptacle connected to the output of the ISO transformer to the other branch circuit wall duplex receptacle hot contact the other audio equipment plugs into. Does it measure zero volts, nominal, or does it measure around 238Vac? IF zero volts, nominal, the two power sources are in phase with one another. IF it measures 238Vac, the two are out of phase with one another. Post back your results.
from the seconds dedicated 20A line to the ISO Trans duplex receptacle outHot to Hot = 0VHot to ground = 118Vso that means the iso trans output is in phase with the 2nd dedicated 20A output circuit
so that means the iso trans output is in phase with the 2nd dedicated 20A output circuit
I bypassed the ISO transformer and the hum is less than half it was from the rewired iso trans...I suppose I should rewire the ISO trans back to what it was or is there something else?
Before you put it back the way it was try reversing the Hot and neutral of the power cord feeding the primary winding of the ISO transformer, at the transformer screw terminals. Check the output voltage at the receptacle and check the AC polarity at the output receptacle again. It will be the same. The only difference will be the Hot contact of the output receptacle will now be in phase with the hot contact of the wall receptacle the transformer is plugs into. Not sure though that will help with the hum.The problem with the way you had it wired originally it is not electrically safe. Both of the secondary leads that were connected to the output duplex receptacle were both hot conductors. The secondary winding was floating above ground.
I bypassed the ISO transformer and the hum is less than half it was from the rewired iso trans...
I went back and reread this post of yours again..... See the thing is, the dedicated circuit that feeds the wall duplex receptacle outlet is fed from a grounded AC power system. The same as you have now with the secondary of the ISO transformer wired as a grounded system. But when you plugged both amps directly into the wall duplex receptacle the hum drops in half.