Let's do some simple math here. The 240 can put out about 120 watts per channel, or about 240 watts of musical power. The "line" fuse, before everything else is 7 amps. This is an internal fuse for the entire amplifier in front of everything even the power transformer. I'm pretty sure the 240/3 is about the same power, but If you want to feel good, let's say it's a 8 amp (guessing) and the 440 may have a 10 amp.
So, the 240 and 240/3 adds up to 15 amps and the 440 is about 10 amps. Now, this is not even the maximum power consumption for these amps as the fuse is a slo-blow. That means the old time element is brought in again. In normal use, the amps may be drawing as little as a few amps each, it depends on how loud you play your music.
Please keep in mind that amplifiers have tremendous inrush current when they are turned on and depending on the condition of the circuit breaker and other additional loads, the 20 amp breaker may trip.
When I consider circuit loads, the amps are the main consideration. If you have only one single 20 amp line, and have these 3 amps on that same circuit, the math says we're 5 amps over, cause the 3 amps are fused to 25 amps. However, again, those fuses will blow at failure mode over time (again, in milliseconds). I was taught that a good rule of thumb on devices like these amps that have variable power consumption is to use 65% as a power factor correction, some suggest 55%. That put's total draw at 16.25 amps @ 65%. Now CD players, preamps and the like can't hardly draw a 1/2 and amp so as it appears to me, the circuit amperage should be OK, unless you have a bunch of these devices. Most CD players are under 25 watts so 25/120 = .2 amps so there is still room.
The problem here is that these amps have a variable power consumption. Let's say we had 20, 100 watt light bulbs on a 15 amp circuit breaker. That would be 20 X 100 or 2,000 watt. Watts divided by volts would be 2,000/120 = 16.666 amps and we would have circuit failure (breaker trips). If we had 18, 100 watt light bulbs, that would be 1800 watts, so 1800/120 = 15. This could be a trip point as well, depending on breaker style (class) and it's trip condition (is it worn). Every time a circuit breaker is tripped, it looses it's holding power a little bit so next time it trips, it may only take 14.95 amps, as an example.
To sum it all up, you have your 20 amp line pretty well consumed. If you plan on adding more equipment, you probably will start to end up in the nuisance tripping mode and it may be necessary to add another branch circuit.
Wayner