I will be expanding the size of my dedicated listening room in the near future and I am currently working the preliminary steps in doing that now. So, I will have a nice opportunity to change how some of my electrical is run. Right now I have a dedicated circuit from my breaker box going to the receptacles that power my system. My system is multi-amped and so I have system receptacles on the wall between my speakers and the ones on the side for the source components. I have the source components connected to a Monarchy isolation transformer now. What I was thinking about was running my entire circuit from the breaker through an oversized industrial isolation transformer, something around 4 to 5KVA. I would probably go 220 in with 110 out. These units are not that expensive considering what we normally pay for our gear. Is this a good idea, or am I way off base here?
Housteau,
I assume you live in the USA.
If you purchase a 5kva transformer and have a licensed electrician in your area install and wire the transformer he will be required to follow the AHJ, (Authority Having Jurisdiction), Code in your area. In most cases AHJ meets and or exceeds NEC Code minimum standard requirements.
Yes the primary should be wired for 240V in and the secondary for straight 120V out.
Also it is a good idea to install the transformer in a room other than where your audio equipment resides.
How much power will a 5Kva transformer deliver at 120V under full load if the primary feeder is sized and fused properly?
5000Va / 120V = 41.67 amps.
You cannot connect your audio system's dedicated branch circuit wiring directly to the secondary of the transformer. That would not meet NEC Code. For one thing the branch circuit wiring would not be big enough. Second, the maximum overcurrent device, breaker, that two NEMA 5-15R 120V 15 amp receptacles, (a Duplex is two), or a NEMA 5-20R 120V 20 amp receptacle is 20 amps.....
The electrician will be required to install a small electrical panel with a main single pole 40 or 50 amp breaker.
A single pole 20 amp breaker will be installed in the panel to feed your existing dedicated circuit providing the branch circuit wire is at least #12 awg.
As for the proper sizing of the wire feeding the primary winding of the transformer the data plate FLA should be used.
5000Va / 240V = 20.8 amps.
20.8 x 125% = 26 amps. Minimum wire size is #10awg copper.
Breaker size?
A couple of options.
1) 125% of data plate primary winding FLA. If FLA is 20.8 amps at 240V, 20.8 x 125% =26. NEC code roll up to a 30 amp 2 pole beaker.
2) Where secondary protection is provided.
Up to 250% of data plate FLA is allowed. You will not need to use this calculation. 125% should be more than enough to handle cold start up inrush current of the transformer with no more connected load that you will have.
The electrician will bond one lead of the secondary winding intentionally to the existing grounding electrode system of your home. This lead will become the Grounded Conductor, the neutral conductor.... The electrician will also bond the transformer enclosure as well as the electrical panel depending on where he decides to bond the neutral conductor and grounding electrode conductor together. He can do it at the transformer or he can do it at the new electrical panel. But not at both. I would prefer at the new electrical panel. (I assume the transformer and new electrical panel will be next to each other.)
>>>>>>>>>
Now a few facts about a common dual winding transformer.
Take for example a single phase 5Kva transformer that is designed and wound to be connected to 240V or 480V and the secondary is designed for 240/120V or straight 120V out.
In your case you will be feeding the transformer with 240V. The 2 primary windings will be connected in parallel.
Secondary? This is where some guys, electricians, mess up. They will wire the transformer for 240/120V volt to feed the new electrical panel. The customer tells the electrician to install the breakers that will be feeding the audio equipment, that will be connected together by ICs, on only one Line, leg, of the panel. In your case, at the present time, you only have one branch circuit.
What is wrong with this picture? Only one winding of the secondary is being used.
Only 2.5Kva, half, of the available power will be in play. Each winding is rated for 2.5Kva. 2500Va / 120V = 20.8 amps.
So in your case you want both windings, observing polarity, wired in parallel. The new panel will be single phase 120V only. Max available amps 41.67.
The above is only intended as a general outline of the wiring method used for a 5Kva power transformer. It is not meant as a complete wiring installation guide.
>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>
Now let’s talk about a so called balanced power system using the same dual primary and dual secondary 5Kva transformer. Can it be wired for balance power? Yes. Did the manufacture design the transformer to be fed by half the data plate voltage rating? No…. But it will work but not as efficient as it would powered within the voltage tolerances of its design.
The 2 primary windings will be connected in series and connect to a 240V source. (Feeding the transformer with half its rated voltage.)
The 2 secondary windings will also be wired in series. The center point of the two windings will be intentionally connected to earth and becomes the neutral, The Grounded Conductor. (Per NEC Code earth will be the grounding electrode system of the main electrical service of your home.) This connection is not used for power. We now have a 120/60V grounded AC power system.
Or more commonly called on audio sites a 60V 0V 60V grounded AC balanced power system.
120V Output per NEC CODE shall be GFCI protected. All 120V branch circuit breakers shall be 2 pole. Also I have to mention it is a violation of NEC Code to install a 120/60V grounded power system in a residential dwelling unit in the USA.
NEC Article 647.3 General
The two secondary windings are in series with one another. Voltage out Line to Line will be 120V nominal. From either hot ungrounded conductor to the neutral conductor will be 60V nominal.
Want to guess what will be the total available output FLA of the name plate 5Kva rated transformer?
20.8 amps max…..
Half the power than if the transformer was wired with the two secondary windings in parallel for 120V out and the primary wired for the data plate rated voltage.
Remember the manufacture designed the transformer to deliver a max of 20.8 amps per secondary winding FLA at the rated data plate connected primary voltage.
Putting the two 60V windings in series will yield a 120V output. But the available max FLA will be the same as if the transformer was 240V out.
5000Va / 240V = 20.8 amps……
http://centralindianaaes.files.wordpress.com/2012/09/indy-aes-2012-seminar-w-notes-v1-0.pdfScroll down to page 200. Worth while reading……
Jim