Hi Rod;
When we bypass the breaker in the 28B for testing, it's actually the amp's own 12A breaker that we are referring to. Also, the 100 and 32 Ampere ratings mentioned are output ratings, not input ratings, so don't let these numbers influence your choices when it comes to rewiring your listening room!
The most current a single 28B can draw from the wall will be 12 Amperes. Because music is not (usually) a continuous signal, even driving it to clipping won't result in this breaker tripping, since the average power will be a fraction of the peak power.
The largest branch circuit that the amp can be plugged into is a 20A dedicated line. In a perfect world, your would have a dedicated 20A line for each 28B, but in real life a single 20A line for both amps would be great. 20 Amp circuits can be used with 15 Amp line cords, so there is no need to upgrade the cord. In fact, if you tried to use a 20 Amp line cord, it couldn't be plugged into the 28B, as this requires a 20 Amp IEC inlet on the amp.